2-family building. One generator. Needs ATS for each family after the POCO meters.
Generac uses six communication wires. 2 wires to send 240V to generator for sensing purposes. 1 wire to charge battery. 3 wires at 12v.
I believe the 3 wires of 12v are for the generator to supply a relay on the transfer switch in between the time the main power goes out and the transfer switch changes over to generator power. And a wire to tell the transfer switch to change over
So I get the impression that I can send the 240 and battery from just one ATS. Then I can parallel from the generator to the transfer switches.
If you are versed in generac, I did 2 yellow and 1 blue from a single ATS to generator. Then I did red, white, and black from generator to both transfer switches.
Will this work? They didn't blow up when I restored utility power after installation. Haven't tested the generator yet. Any other thoughts?
Generac uses six communication wires. 2 wires to send 240V to generator for sensing purposes. 1 wire to charge battery. 3 wires at 12v.
I believe the 3 wires of 12v are for the generator to supply a relay on the transfer switch in between the time the main power goes out and the transfer switch changes over to generator power. And a wire to tell the transfer switch to change over
So I get the impression that I can send the 240 and battery from just one ATS. Then I can parallel from the generator to the transfer switches.
If you are versed in generac, I did 2 yellow and 1 blue from a single ATS to generator. Then I did red, white, and black from generator to both transfer switches.
Will this work? They didn't blow up when I restored utility power after installation. Haven't tested the generator yet. Any other thoughts?