I have a question about wiring a genset for a farm that is fed from 2 services.

Customer bought a 250A genset to feed his farm. Main farm service is 400A. Opposite end of the farm has a separate, 200A service, from a separate utility transformer that feeds 2 hog barns. Hog barn was wired with a 200A 2pole ATS 10 years ago to feed barns in case of outage. Recently customer ran underground wire from main farm service to hog barn service and wants to power both services from the new genset located in the hog barn.

I understand that this genset should be installed as a SDS, which means the ATS and main farm service will need a neutral break. Cost is driving factor and it'd be about 5K to put in new ATS guts with a neutral break and a 3P manual switch for the farm. How important is it to have a neutral break option in this situation? Will a shared neutral path from the two services really be an issue?
 

qcroanoke

Sometimes I don't know if I'm the boxer or the bag
Location
Roanoke, VA.
Occupation
Sorta retired........
I have a question about wiring a genset for a farm that is fed from 2 services.

Customer bought a 250A genset to feed his farm. Main farm service is 400A. Opposite end of the farm has a separate, 200A service, from a separate utility transformer that feeds 2 hog barns. Hog barn was wired with a 200A 2pole ATS 10 years ago to feed barns in case of outage. Recently customer ran underground wire from main farm service to hog barn service and wants to power both services from the new genset located in the hog barn.

I understand that this genset should be installed as a SDS, which means the ATS and main farm service will need a neutral break. Cost is driving factor and it'd be about 5K to put in new ATS guts with a neutral break and a 3P manual switch for the farm. How important is it to have a neutral break option in this situation? Will a shared neutral path from the two services really be an issue?
How are you going to hook the generator output to the 400 amp service in the main barn?
To me you would need a Manual transfer switch in front of the 400 amp service to disconnect the service.
And I'm not so sure you could legally do that with two Seperate services and one genset.
Let's see what others have to say.
 
Location
MN
Occupation
Electrical Contractor
There is an existing manual DPDT switch (no neutral break) on the load side of the 400A disconnect. Wires feed to multiple buildings after that. Load will never be that much, it was sized that large for a bin dryer about 5 years ago. I have read some other posts on gensets and I can't seem to determine if it matters that there are 2 utility transformers for the 2 services vs 1 xfmr and 2 services. Will neutral current flow to utility transformer if this generator is not separately derived? I do not want to put line man at risk...
 

hillbilly1

Senior Member
Location
North Georgia mountains
Occupation
Owner/electrical contractor
There is an existing manual DPDT switch (no neutral break) on the load side of the 400A disconnect. Wires feed to multiple buildings after that. Load will never be that much, it was sized that large for a bin dryer about 5 years ago. I have read some other posts on gensets and I can't seem to determine if it matters that there are 2 utility transformers for the 2 services vs 1 xfmr and 2 services. Will neutral current flow to utility transformer if this generator is not separately derived? I do not want to put line man at risk...
Very unlikely, but always a possibility the utility neutral current may flow through the generator if the utility hv ground/ Neutral line gets broken, and their hot is still connected.
 

Fred B

Senior Member
Location
Upstate, NY
Occupation
Electrician
2 services will require 2 ATS. like described here:

Of course with 2 separate services from 2 separate transformers it would really require SDS configuration that will switch the neutral. A power outage could in theory could result in only one structure loss of power and sharing a neutral could energize to the down side of the system endangering the lineman.

Also a load calculation would need to be done to ensure the genset is not overloaded while powering the what looks like a potential of 600A between the 2 services. Potential for load shedding might also be considered.
Recently customer ran underground wire from main farm service to hog barn service and wants to power both services from the new genset located in the hog barn.
This factor really not your concern as it sounds like a start of a DIY by the farmer that he got lost in. If the customer unwilling to fund correct installation its a better run away than try to cob something together to save them money. see no CHEAP options.
 

wwhitney

Senior Member
Location
Berkeley, CA
Occupation
Retired
Of course with 2 separate services from 2 separate transformers it would really require SDS configuration that will switch the neutral. A power outage could in theory could result in only one structure loss of power and sharing a neutral could energize to the down side of the system endangering the lineman.
I don't see how having one solidly connected conductor could energize a system in a way that would endanger a lineman.

But I do believe that with two separate services it would be a violation of 250.24(A)(5). Avoiding that violation would only require one of the two ATSs to switch the grounded conductor; the other could use a solidly connected grounded conductor.

Cheers, Wayne
 