poopdeckpappy
Member
- Location
- Franklin, LA
Remodel project where all raceways and boxes are bricked in, making substantial modifications unappealing.
New surface mounted load center being installed and connected to several existing boxes in the wall to which all existing raceways connect. Considering a wireway to connect the new load center to the old boxes.
Supposing that the conductor fill in the wireway and existing boxes will be OK, does anyone see a violation pulling one appropriately sized neutral conductor from the load center to an existing box along with the branch circuit protected L1, L2 & L3 conductors and installing a listed neutral bar in the existing boxes to serve as the point of connection.
One large neutral goes a long way in keeping conductor count below 30 to keep from having to derate.
Why not just use sub panels at the different locations, you ask? Insufficient working space.
New surface mounted load center being installed and connected to several existing boxes in the wall to which all existing raceways connect. Considering a wireway to connect the new load center to the old boxes.
Supposing that the conductor fill in the wireway and existing boxes will be OK, does anyone see a violation pulling one appropriately sized neutral conductor from the load center to an existing box along with the branch circuit protected L1, L2 & L3 conductors and installing a listed neutral bar in the existing boxes to serve as the point of connection.