One line diagram

One line diagram

Installing a 120/208 3 phase system on a existing building (retail store front interior buildout or strip mall); service size is 320 amp using parallel wires coming from an existing gutter box 6 ea. 2/O, 2 ea. 1/O and 2 ea. #6 utilizing a 3" conduit, 1 ea. disconnect 400 amp fused at 320...Let me know what else you need to know...Many thanks for your assistance
 
Info

Info

Nomad,
Need a couple things,
Size of main service feeding this existing gutterbox.
Is there a ct cabinet also? and metering?
As i see it ,your new 400 amp switch fused at 320 will be feeding what?
Perhaps a 40 circuit- 3 phase- 120/208 volt 400 amp panel?
Also what is coming from this new distribution panel, maybe a panel schedule will help if you have.
I just want to know all the pieces of the puzzle so i don't mis-inform you with a diagram.
 
tool

tool

I use an old architectual program that does one line diagrams, also has a newer one called smart draw, They have some one line diagrams already done for you. All you must do is change some figures.
 
Last edited:
Here's one from a small job we're doing right now:

1line.jpg
 
petersonra said:
ground rods? no CEE?
Older existing building, all brick, no access to CEE (if there is even rebar at all), new all-plastic plumbing, connection to fire-sprinkler system not permitted.

Ground rods. In fact, if I'm not mistaken, we only need a single rod, of which there already is one. 2002 NEC, by the way.
 
RUWIREDRITE said:
Nomad,
Need a couple things,
Size of main service feeding this existing gutterbox.
Is there a ct cabinet also? and metering?
As i see it ,your new 400 amp switch fused at 320 will be feeding what?
Perhaps a 40 circuit- 3 phase- 120/208 volt 400 amp panel?
Also what is coming from this new distribution panel, maybe a panel schedule will help if you have.
I just want to know all the pieces of the puzzle so i don't mis-inform you with a diagram.
The service from the existing gutter box comes straight from the light company's transfomer 12470 v primary and 120/208 three phase secondary, each tranformers is rated at 50 kva, out of the gutter box there no CT can and there will only be 1 meter socket @ 320 amp and then there will be a 400 disconnet fused at 320 amps which will be feeding 2 ea. 200 amp load centers. No panel schedule Im still trying to wing that one :).
 
Dnkldorf said:
Larry, what program is that?
Patricia (my better third) did these drawings from scratch with Paint Shop Pro. Want to see more, like the rear elevation, panels scehdules, etc?
 