hotblueelectric
Member
- Location
- Dallas Texas
Have a customer ( retired utility guy) who has 1 small shop in his back yard and is building a larger one in back. His 200a panel is pretty full so he wants to add a new panel outside his garage. I told him we would have to install a new meterbase 320A. The meterbase (double load side lugs) would feed the home then feed a small outdoor 125 amp panel with a 25 amp cb for the small shop and a 100A cb for the larger shop. I consider the new panel a separate system and this is the the disconnect for the shops. I told him we would bond the neutral in the new panel to ground, run a # 6 ground to his existing ground rod, and run grounds from the new panel to both buildings. At both shops we would NOT bond the neutral to ground. He disagrees with me and has has bonded both shops neutral bars. He insists he is correct. I disagree.
Any feed back appreciated.:roll::roll:
Any feed back appreciated.:roll::roll: