Explain it to me again please.
How does a fault on a 20 amp circuit blow a 100A fuse without tripping a breaker? I've seen it happen more than once.
------------------------------
Part two. How do all 3 100A fuses blow without tripping any downstream breakers?
Situation:
277/480V 3 phase source.
100A switch in 1000A section feeds panel via ATS. ATS is not operational. Installed but for some reason, no control wiring hooked up, never has been.
Lighting load = 14, 20A, 277V citcuits for office lights and 10, 20A, 277V circuits for alll the HID high bay fixtures in warehouse (controled by contactors)
Additional loads:
One, 60A, 480V 3 phase 4wire feed to guard shack appx 1000' away with 120/208, 3 phase transformer and panel.
One, 20A 480V single phase 3 wire feed to gate operator 1000' away. Small 120/208 trannsformer for gate equipment.
SKOP (standard knucklehead operating procedure) is to replace fuses and turn things back on one at a time. Everything comes back on, A phase = about 60A, B and C are about 50 something. No signs of trouble at breakers, contactors, ATS connections or discos.
Old fuses were Bussman LPS-RK
New fuses are different MFG, FSLP. Chart at the supply house says they match. I am clueless what the fuse rating numbers/letters mean.
Realization. Did a breaker trip and they reset it without telling me? Possible I guess.
How does a fault on a 20 amp circuit blow a 100A fuse without tripping a breaker? I've seen it happen more than once.
------------------------------
Part two. How do all 3 100A fuses blow without tripping any downstream breakers?
Situation:
277/480V 3 phase source.
100A switch in 1000A section feeds panel via ATS. ATS is not operational. Installed but for some reason, no control wiring hooked up, never has been.
Lighting load = 14, 20A, 277V citcuits for office lights and 10, 20A, 277V circuits for alll the HID high bay fixtures in warehouse (controled by contactors)
Additional loads:
One, 60A, 480V 3 phase 4wire feed to guard shack appx 1000' away with 120/208, 3 phase transformer and panel.
One, 20A 480V single phase 3 wire feed to gate operator 1000' away. Small 120/208 trannsformer for gate equipment.
SKOP (standard knucklehead operating procedure) is to replace fuses and turn things back on one at a time. Everything comes back on, A phase = about 60A, B and C are about 50 something. No signs of trouble at breakers, contactors, ATS connections or discos.
Old fuses were Bussman LPS-RK
New fuses are different MFG, FSLP. Chart at the supply house says they match. I am clueless what the fuse rating numbers/letters mean.
Realization. Did a breaker trip and they reset it without telling me? Possible I guess.