So, my calculation based on an old Visual Basic program-I did it myself 20 years ago-it is not a modern one based on ETAP or else. The advantage is that I can modify it as I like it.
Now, as an answer to your question. Actually, in our design, we used schedule 80 pvc duct for concrete duct bank and not art.352 schedule 40 as I indicated above. The available cross section it is less but still enough.
If we refer to the MCC actual load I think we always take the MCC rated as cable possible load. I think I can consider only 3 busy ducts instead of 4-since the 4thd is reserve.
Another possibility is to check the voltage drop. Let say 3% at 200 feet length 3 parallel cables at 3*480 V rated the voltage drop is 14.4 V then 14.4/1.73/0.04/0.2[see chpt.9 Tab.9 NEC]=1039 A and 346 A per cable.
I have to try other possibilities: increase the distance between ducts may I can get 200 A ,for instance.
The demand factor of 0.6 [60%] may be also.