medinajuli
Member
- Location
- Florida
- Occupation
- Engineer
Hi Dears, I have a Disconnect switch of 400A that feed two panels of 200A each one, for these panels is necessary individual protection of 200 MCB? According to 408.36? Tks.
My apologies dear, but when you answer my question, "for these panels is necessary individual protection of 200 MCB?" you said yes.I don't understad the reason for your post. You seem to be answering your own question. Each panel in the exhibits has OCP n ot exceeding the panel rating.