My question is if I have three service masts coming down from an overhead entrance(3 weatherheads) to three seperate 400 amp fused main discos and each disco feeding a 400amp panel...do i have have three 400 amp services or one 1200 amp service?:confused:
 

kwired

Electron manager
Location
NE Nebraska
My question is if I have three service masts coming down from an overhead entrance(3 weatherheads) to three seperate 400 amp fused main discos and each disco feeding a 400amp panel...do i have have three 400 amp services or one 1200 amp service?:confused:

Unless each one is of different voltage/frequency/phase and comes from a different service drop, you have one service.


230.71 Maximum Number of Disconnects.

(A) General. The service disconnecting means for each service permitted by 230.2, or for each set of service-entrance conductors permitted by 230.40, Exception No. 1, 3, 4, or 5, shall consist of not more than six switches or sets of circuit breakers, or a combination of not more than six switches and sets of circuit breakers, mounted in a single enclosure, in a group of separate enclosures, or in or on a switchboard. There shall be not more than six sets of disconnects per service grouped in any one location.
 