Question on multiple metering with service disconnets. Here is the situation.
a 4-story building. There will be multiple tenants on each floor, probably 8 to 9. I am going to have a 2500A 120/208v service for the building. My design is following.
One service lateral from utility xfmr to a 2500A swbd on the first floor. The swbd will have (5) circuit breakers without a main. I am intending to use this as service disconnects per six disconnect rule per 230.71. Each circuit breaker feeds a termination box on each floor which will feed a meter bank (up to (9) meters)for multiple tenants on that floor.
For example, a 800A circuit breaker at switchbord will feed a 800A termination box on the second floor. Off of that termination box, there will be a meterbank with (9) meters for multiple tenants. Each meter will have a tenant circuit breaker.
Now my question is
1) Is this complied with the code?
2) Can I have (1) remote service disconnect with multiple meters like I intended?
3) Or Should each tenant circuit breaker be considered as a service disconnet? If this is the case, should the meter bank be limited to 6 at each location per 230.71 (six disconnect rule)? Then I will have to have two meterbanks at each floor.
I appreciate your responses in advance.
[ October 18, 2005, 10:53 AM: Message edited by: jkim780 ]
a 4-story building. There will be multiple tenants on each floor, probably 8 to 9. I am going to have a 2500A 120/208v service for the building. My design is following.
One service lateral from utility xfmr to a 2500A swbd on the first floor. The swbd will have (5) circuit breakers without a main. I am intending to use this as service disconnects per six disconnect rule per 230.71. Each circuit breaker feeds a termination box on each floor which will feed a meter bank (up to (9) meters)for multiple tenants on that floor.
For example, a 800A circuit breaker at switchbord will feed a 800A termination box on the second floor. Off of that termination box, there will be a meterbank with (9) meters for multiple tenants. Each meter will have a tenant circuit breaker.
Now my question is
1) Is this complied with the code?
2) Can I have (1) remote service disconnect with multiple meters like I intended?
3) Or Should each tenant circuit breaker be considered as a service disconnet? If this is the case, should the meter bank be limited to 6 at each location per 230.71 (six disconnect rule)? Then I will have to have two meterbanks at each floor.
I appreciate your responses in advance.