one wire

Status
Not open for further replies.

guschash

Senior Member
Location
Ohio
where in the code does mention only one wire on a breaker ? One wire per neutral bar, ground bar no more three and I know breakers should not have more one wire. I think Cutter Hammer has captures so they can two. Where in code does it talk about one wire under a screw. I looked article 110 and article 230 .
 
where in the code does mention only one wire on a breaker ? One wire per neutral bar, ground bar no more three and I know breakers should not have more one wire. I think Cutter Hammer has captures so they can two. Where in code does it talk about one wire under a screw. I looked article 110 and article 230 .
It will be contained in the UL listing for the breaker.
 
where in the code does mention only one wire on a breaker ? One wire per neutral bar, ground bar no more three and I know breakers should not have more one wire. I think Cutter Hammer has captures so they can two. Where in code does it talk about one wire under a screw. I looked article 110 and article 230 .
110.14.(A)
 
where in the code does mention only one wire on a breaker ? One wire per neutral bar, ground bar no more three and I know breakers should not have more one wire. I think Cutter Hammer has captures so they can two. Where in code does it talk about one wire under a screw. I looked article 110 and article 230 .
QO and Homeline accept 2 wires.
Don't believe Siemens accepts 2
 
where in the code does mention only one wire on a breaker ? One wire per neutral bar, ground bar no more three and I know breakers should not have more one wire. I think Cutter Hammer has captures so they can two. Where in code does it talk about one wire under a screw. I looked article 110 and article 230 .
The only thing specifically mentioned in the NEC is one grounded conductor per hole. For ground bar and breakers, it just per the listing/instructions...
 