the question reads
what is the general lighting and general use receptical load for a 30,000 sq ft bank
a162kva
b123kva
c173 kva
d 151 kva
I think none are right
30,000 x 3.5 va sqft for lights as per 230.12 105,000
30,000 x 1 va per sqft for outlets as per 230.14k
30,000
the first 10,000 100% as per 220.44 10,000
the rest 50% 20,000 x.50 10,000
125,000va or 125kva
am i going a stray somewhere