Maybe a dopey question, but are there any code references on wiring only 1 pole of a 2 pole breaker (is it ok to wire only 1 pole)?
I've never seen a panel with expansion slots. My computer has a few, but I've never seen a panel with even one.Originally posted by tonype:
Also, are there any safeguards to prevent a HO from looking in and thinking that this is an expansion slot?
This would be code compliant also. There is no code reason you could not have a two pole breaker protecting two entirely different circuits.Originally posted by tonype:
what I was trying to say is that a HO could be adding a circuit and view the unused pole as a convenient place to power the wire. Wouldn't this result in two separate circuits being protected by one breaker that has a handle tie connecting the poles? Or am I looking too far into this?
Could I please have an example of this? I am very interested in seeing that.This would be code compliant also. There is no code reason you could not have a two pole breaker protecting two entirely different circuits.
As a mater of fact in some instances it is required.
Of course this could be accomplished with the properly listed two pole switch but using a two pole breaker or two single pole breakers with handle ties would be easer.210.7 Branch Circuit Receptacle Requirements.
(C) Multiple Branch Circuits. Where more than one branch circuit supplies more than one receptacle on the same yoke, a means to simultaneously disconnect the ungrounded conductors supplying those receptacles shall be provided at the panelboard where the branch circuits originated.
Just curious how you would do it if you rule out a double pole breaker or a two pole switch?Originally posted by milwaukeesteve:
Bob, I believe I have heard this argument before, but nothing is being said.
First, in this code rule it says a means to simultaneously disconnect ... shall be provided.. at the panelboard where the branch circuits originate.
Where does it say that it is legal to install a double pole breaker for this installation in this code rule?
Where also does it say that a double pole switch can be used if you need to simultaneously disconnect where the circuit originates?
Where is the info that prohibits either of those scenarios?Originally posted by milwaukeesteve:
Where is the manufacturer rating that identifies the double pole breaker for use with 2 individual circuits?
For that matter, where is the manufacturer rating for double pole breakers to be used for individual single circuits (using only 1 of 2 poles)?
Thats right all it requires is "a means to simultaneously disconnect the ungrounded conductors supplying those receptacles" They did not specify handle ties, common trip breakers, two pole switches or even relays.Originally posted by milwaukeesteve:
Manufacturer listed handle ties are a 'provide means to simultaneously disconnect'.
This code section is not asking for 'automatic' trip. It only requires that a means for disconnecting be provided.
Steve the requirement requires the 'means' to be at the panel not in the panel.Originally posted by milwaukeesteve:
Your idea of a 2 pole switch can't work because it says where the circuit originates.
It's your right to believe that but IMO you are mistaken. If the writers specifically wanted handle ties the section would say "approved handle ties"Originally posted by milwaukeesteve:
I believe that this code rule is specifically looking for handles from separate breakers to be 'tied' together. Especially from the way the rule is worded 'a means.. shall be provided'. As in that the breakers are already there, and we need to tie them together.
Actually it is just that, we can do whatever we dream up unless a code article says otherwise.Originally posted by milwaukeesteve:
Permissive code is not a blank check for you to do what ever you want.
Larry I think you are forgetting the 120 part of 240/120.Originally posted by LarryFine:
Actually, that means it is okay to feed line-to-line loads.