Only 1 pole of a 2 pole breaker used

Status
Not open for further replies.

tonype

Senior Member
Location
New Jersey
Maybe a dopey question, but are there any code references on wiring only 1 pole of a 2 pole breaker (is it ok to wire only 1 pole)?
 
Re: Only 1 pole of a 2 pole breaker used

Yes, you can use only one pole of a 2 or 3 pole CB.
 
Re: Only 1 pole of a 2 pole breaker used

Infinity: Do you need to ID the breaker in any manner? Also, are there any safeguards to prevent a HO from looking in and thinking that this is an expansion slot?
 
Re: Only 1 pole of a 2 pole breaker used

As a general NEC rule all CB's must be labeled. You could label one pole for it's intended use and label the other pole as a spare. You lost me on the expansion slot thing.
 
Re: Only 1 pole of a 2 pole breaker used

Originally posted by tonype:
Also, are there any safeguards to prevent a HO from looking in and thinking that this is an expansion slot?
I've never seen a panel with expansion slots. My computer has a few, but I've never seen a panel with even one.
 
Re: Only 1 pole of a 2 pole breaker used

Maybe I do not have the lingo correct (I am a home inspector/engineer always looking to improve myself via this forum) - what I was trying to say is that a HO could be adding a circuit and view the unused pole as a convenient place to power the wire. Wouldn't this result in two separate circuits being protected by one breaker that has a handle tie connecting the poles? Or am I looking too far into this?
 
Re: Only 1 pole of a 2 pole breaker used

Originally posted by tonype:
what I was trying to say is that a HO could be adding a circuit and view the unused pole as a convenient place to power the wire. Wouldn't this result in two separate circuits being protected by one breaker that has a handle tie connecting the poles? Or am I looking too far into this?
This would be code compliant also. There is no code reason you could not have a two pole breaker protecting two entirely different circuits.

As a mater of fact in some instances it is required.
 
Re: Only 1 pole of a 2 pole breaker used

This would be code compliant also. There is no code reason you could not have a two pole breaker protecting two entirely different circuits.

As a mater of fact in some instances it is required.
Could I please have an example of this? I am very interested in seeing that.

edit: Please include NEC article

[ October 25, 2005, 03:28 PM: Message edited by: milwaukeesteve ]
 
Re: Only 1 pole of a 2 pole breaker used

2002 NEC

Notice this section is not about multiwire branch circuits.

210.7 Branch Circuit Receptacle Requirements.

(C) Multiple Branch Circuits. Where more than one branch circuit supplies more than one receptacle on the same yoke, a means to simultaneously disconnect the ungrounded conductors supplying those receptacles shall be provided at the panelboard where the branch circuits originated.
Of course this could be accomplished with the properly listed two pole switch but using a two pole breaker or two single pole breakers with handle ties would be easer.

By the way in 2005 the rules have changed and moved but are still there.

[ October 25, 2005, 03:36 PM: Message edited by: iwire ]
 
Re: Only 1 pole of a 2 pole breaker used

Bob, I believe I have heard this argument before, but nothing is being said.
First, in this code rule it says a means to simultaneously disconnect ... shall be provided.. at the panelboard where the branch circuits originate.
Where does it say that it is legal to install a double pole breaker for this installation in this code rule?
Where also does it say that a double pole switch can be used if you need to simultaneously disconnect where the circuit originates?
Where is the manufacturer rating that identifies the double pole breaker for use with 2 individual circuits?
For that matter, where is the manufacturer rating for double pole breakers to be used for individual single circuits (using only 1 of 2 poles)?
 
Re: Only 1 pole of a 2 pole breaker used

Originally posted by milwaukeesteve:
Bob, I believe I have heard this argument before, but nothing is being said.
First, in this code rule it says a means to simultaneously disconnect ... shall be provided.. at the panelboard where the branch circuits originate.
Where does it say that it is legal to install a double pole breaker for this installation in this code rule?
Where also does it say that a double pole switch can be used if you need to simultaneously disconnect where the circuit originates?
Just curious how you would do it if you rule out a double pole breaker or a two pole switch?

Originally posted by milwaukeesteve:
Where is the manufacturer rating that identifies the double pole breaker for use with 2 individual circuits?
For that matter, where is the manufacturer rating for double pole breakers to be used for individual single circuits (using only 1 of 2 poles)?
Where is the info that prohibits either of those scenarios?

I know you hate it but the NEC is a permissive code, if it does not say you can not.....you can. :)


Steve you must accept that, it is a fact.
 
Re: Only 1 pole of a 2 pole breaker used

Manufacturer listed handle ties are a 'provide means to simultaneously disconnect'.
This code section is not asking for 'automatic' trip. It only requires that a means for disconnecting be provided.
Your idea of a 2 pole switch can't work because it says where the circuit originates.

I believe that this code rule is specifically looking for handles from separate breakers to be 'tied' together. Especially from the way the rule is worded 'a means.. shall be provided'. As in that the breakers are already there, and we need to tie them together.


We can go round and round about the permissive code issue. My argument is that we push that permissive issue too far. We take wording that could mean something to say that it does mean something. We say that since it didn't say someting, that I can do something.
Alot of the arguments I have had are on code rules where it specifically tells you the things you CAN do, yet when someone wants to do something else, they say that the article doesn't say CAN'T. The article isn't trying to tell you the CAN'Ts, but rather only the CANs.

Permissive code is not a blank check for you to do what ever you want.
 
Re: Only 1 pole of a 2 pole breaker used

Originally posted by milwaukeesteve:
Manufacturer listed handle ties are a 'provide means to simultaneously disconnect'.
This code section is not asking for 'automatic' trip. It only requires that a means for disconnecting be provided.
Thats right all it requires is "a means to simultaneously disconnect the ungrounded conductors supplying those receptacles" They did not specify handle ties, common trip breakers, two pole switches or even relays.

That means without "pushing the code" it is up to the installer to come up with an acceptable means to a means to simultaneously disconnect the ungrounded conductors.

Originally posted by milwaukeesteve:
Your idea of a 2 pole switch can't work because it says where the circuit originates.
Steve the requirement requires the 'means' to be at the panel not in the panel.

They carefully worded it so that you could use other means than a breaker at all. Lets say you where feeding two circuits to one yoke from a fuse panel, you would have to use a switch at the panel.

Originally posted by milwaukeesteve:
I believe that this code rule is specifically looking for handles from separate breakers to be 'tied' together. Especially from the way the rule is worded 'a means.. shall be provided'. As in that the breakers are already there, and we need to tie them together.
It's your right to believe that but IMO you are mistaken. If the writers specifically wanted handle ties the section would say "approved handle ties"

Originally posted by milwaukeesteve:
Permissive code is not a blank check for you to do what ever you want.
Actually it is just that, we can do whatever we dream up unless a code article says otherwise.

Tell me where is the code section that says I can install a panel in a kitchen, or garage or bedroom etc? :p
 
Re: Only 1 pole of a 2 pole breaker used

Looking up some info on Square D Homeline breakers, most of their 2-pole breakers are dual rated 120/240. That would tell me that it is ok to install 2 - 120V circuits on a 2-pole breaker.
 
Re: Only 1 pole of a 2 pole breaker used

Actually, that means it is okay to feed line-to-line loads.
 
Re: Only 1 pole of a 2 pole breaker used

Actually the slash rating of 120/240V says a breaker is rated for line to line voltages of 240V but the line to ground voltage is only 120V maximum (which means it cannot be used on a 240V to ground system).

UL Listed breakers have been tested for all combinations of loads including 1P only on a 2P breaker and 1P and 2P only on 3p breakers.
 