Is there a code that says anything about a certain number of wires allowed in a conduit 3 feet and under?
Is there a code that says anything about a certain number of wires allowed in a conduit 3 feet and under?
The 9 wires comes up often because with a 90C wire usually the derating that is necessary will not affect the final ampacity at the 75C rating until you have more than 9 conductors.
For instance, #12 THHN is rated 30 amps and must be derated 70% for 9 CCC however that still leaves us with 21 amps so the circuit is not affected by the 9 conductors. It has nothing to do with in the ground unless you have a local ordinance
But before anyone jumps too deeply into that thumb rule pool, be advised that for 30 amp circuits and #10 wire, a similar mathematical process will conclude that the "magic number" is 6.
Yep that one stumps a few because they don't look at the ratio or percent difference between the allowed rating and the 90?c rating, they just look at the 10 amp difference across the board and think they are all the same.
#14= 15 amp allowed, 25 amp 90?c rating = 10 amps but a 60% difference
#12= 20 amp allowed, 30 amp 90?c rating = 10 amps but a 661/3% difference
#10= 20 amp allowed, 40 amp 90?c rating = 10 amps but a 75% difference
so it is this that causes a #10 to have only a 28 amp rating when 9 conductors are installed into a conduit, while #12 will have a 21 amp rating, and #14 will have a 17.5 amp rating
and at 28 amps,in most cases, you can still use a 30 amp ocpd
And I agree but, I don't think the OP's question nor the answers are aimed at buried installations.Actually gentlemen, this question DOES have EVERYTHING to do with the three foot under part of the question. Case in point, see the controlling article 300.5, where a raceway (ANY raceway) is buried below grade, THAT interior is a wet rated location. So then referencing 310.104(A), a lot of insulation types (most actually) are restricted to the 75 degree column where installed in a wet location-even if you have the other two items needed when using the 90 degree column... (Also see 310.10(B) & (C), conductors rated for dry-damp, or wet locations.
Hope my input helps.
Actually gentlemen, this question DOES have EVERYTHING to do with the three foot under part of the question. Case in point, see the controlling article 300.5, where a raceway (ANY raceway) is buried below grade, THAT interior is a wet rated location. So then referencing 310.104(A), a lot of insulation types (most actually) are restricted to the 75 degree column where installed in a wet location-even if you have the other two items needed when using the 90 degree column... (Also see 310.10(B) & (C), conductors rated for dry-damp, or wet locations.
Hope my input helps.