Only one conductor per terminal?

Merry Christmas

Dale001289

Senior Member
Location
Georgia
Is this a true statement?:
"Control wiring should have only one conductor per terminal unless otherwise Listed for more than one." This is coming from one of the inspectors, but I cant seem to find that language in the NEC.
 
(OK, Infinity beat me to the draw on this one. But I'll post it anyway.)

How about the "catch all" that tells us to comply with the instructions in the product's listing?
 
Yes in most cases it will be a control panel application
I think just about every industrial control panel I've ever worked on had more than one conductor under a DIN rail terminal. I'm not sure if those terminals are listed for more than one conductor or if ANSI/UL 508A Standard for Industrial Control Panels actually permits it. Either way if it's part of a listed control panel IMO the NEC doesn't apply to how it's wired in the factory.
 
I'm not sure if those terminals are listed for more than one conductor or if ANSI/UL 508A Standard for Industrial Control Panels actually permits it.
I don't think I have ever seen a terminal block that was not rated for at least (2) #12AWG control size conductors.
I know the panels I built under UL508A often had multiple conductors in terminals.
 
I don't think I have ever seen a terminal block that was not rated for at least (2) control size conductors.
Jim, where would you find that information? I don't recall seeing it on a label in the control panel. Here's an example of factory wiring with more than one conductor under a terminal:
Sub-meter panel 001.jpg
 
It would be found in the terminal manufacturer's literature.
If the terminal has multiple conductors and is part of the factory wiring (as in the photo in post #11) is it covered under the NEC? I say no if it's in a listed control panel and therefore the inspector should have nothing to say about the factory wiring.
 