Yoyo

New member
Location
Carle Place Ny
Ok. So I am trying to figure out if this is a code violation on some work that's already been done. So there is a 400 amp main out on a service stand. Out of the 400 amp main, there are two parallel 3/0 3 conductor MCHL cables feeding a distribution gutter 200 ft away. Out of this distribution gutter, two more parallel 3/0 conductors feed a disconnect which then goes to a VFD and on to a 480 volt, 200 horse motor. That's all understandable, but my issue is this distribution gutter, there is another set of 3/0 conductors on the load side feeding a sub panel with a 200 amp main breaker. The "200 amp" breaker only feeds a 20 amp breaker for a paneltrans and a 20 amp breaker for a block heater). So I'm using 30 amps out of the 200. If it were me, I would have just installed a 600 amp main, distributed to the vfd and sub panel and not worried about it, but I am worried that it's a code violation simply because that main is 200 amps. The motor at 1.25 is about 300 amps, so I know that my wire size is ok and it won't overload the circuit. I'll only be using like 330 amps max but I just don't know if the inspector will look at the distribution gutter feeding a 400 amp disco and 200 amp main breaker and say it's wrong. Please help and thanks
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Once you tap off of the parallel 3/0s with a single set, that tap to your 200 amp panel would need to meet the appropriate tap rule in 240.21. If thats the case it seems compliant
 
Status
Not open for further replies.
Top