A buddy called me yesterday and said he got wrote up on a Large Pull Box that was installed for feeders. It was for a strait pull without a splice. I thought wow, dumb mistake, but then he told me the inspector counted the 8 times the diameter from where the fittings ended inside the box. 2" emt connector with a plastic bushing on the end sticks into the box a little bit. I was dumb founded and it took my breath away! I guess I have many, many installations that don't meet code!! He was really bumbed because it was going to take a bit of work as you guys can imagine to fix the situation. I feel bad for him as well, because I would have been in the exact boat.