oops??

Status
Not open for further replies.

nizak

Senior Member
Did my first pool job this week, pool contractor filled pool and didn't say anything about wet niche fixture being installed. Also, #8 insulated CU ground was not pulled in. Am I screwed on the ground and terminating it in the shell? Another dumb ??, apparently the conduit fills with water as well in a wet nich app. Thanks.
 

nizak

Senior Member
Wouldn't the fixture and appropriate wiring be installed after the liner was in and before the water level exceeded the opening?
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Get your suit on and enjoy the install. I never wire them since the pool contractors do that end of it but I think it can be done with the water in the pool. You should be able to ground the niche but you will need to pull a #8 in there.
 

nizak

Senior Member
Dennis, not being at all familiar with the sequence of events, is it a common practice to install the light after the water is in? I was in the house most of the day working in the basement, nobody said a word about putting in the light. Also, the conduit is going to be full of water to a certain point, is that common as well?
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Get your suit on and enjoy the install. I never wire them since the pool contractors do that end of it but I think it can be done with the water in the pool. You should be able to ground the niche but you will need to pull a #8 in there.

I have never seen a required listed potting compound that can be applied underwater
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
I have never seen a required listed potting compound that can be applied underwater
Yes, I forgot about that.

To answer nizak- I have never seen the lights go in after the water was filled. That was just dumb. I was thinking about changing the bulb not encapsulating with the compound.
 

SEO

Senior Member
Location
Michigan
Some pool installers have barricade that goes around the wet niche area that is held onto the pool walls with suction. When it is applied it will trap around 10 gallons of water that can be pumped out then you can apply the potting compound and ground wire. Otherwise you will probably have to drain the pool to a level where you can do your work.
 

bradleyelectric

Senior Member
Location
forest hill, md
The water will go in the conduit. That is not an issue. Your issue is the potting conpound that is required at the insulated #8 termination in the niche. The conduit is required to run from the niche to the "deck box". The deck box has location and height requirements along with sealing requirements to keep the water off terminations in it.

The way we do it is the pool installer sets his frame or rebar and installs the niche. We run conduit from the niche to our deck box. We pull in the #8 and a string and do the potting. Call in trench inspection on the niche conduit and have potting inspected. You want to make sure you only run the male terminal into the niche far enough to make it even with the niche on the inside or it will hold the light from seating properly. Make sure you seal the threads good though or the water will leak out of the pool through your threads.

The pool installer uses the string to pull the light in when he installs the liner or after the concrete is shot and before the plaster is installed. The light can be changed after the water is in the pool, but I don't know of a way to do the potting. We do the terminations in the deck box when we return after the equipment is set. These are inground pools. If you are talking about an above ground pool then they should have given you time to do the niche. At least they don't usually have as much water that needs to be drained.
 

nizak

Senior Member
I'm sure that it is going to be the electricians fault! I can't believe that the guy wouldn't have said something,best part of the whole thing is that he is supplying the fixture and that his worker told me it would be here tomorrow. What am I missing???
 

nizak

Senior Member
bradley, on your inground pools is it fairly common to install the wet niche fixtures after the pool is filled?
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
bradley, on your inground pools is it fairly common to install the wet niche fixtures after the pool is filled?
Nizak, that is not the way it is normally done. No one in there right mind would choose to do it that way unless they were changing it out. As stated you have to use a potting compound on the ground wire and you cannot do that when it is filled with water.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
I'm sure that it is going to be the electricians fault! I can't believe that the guy wouldn't have said something,best part of the whole thing is that he is supplying the fixture and that his worker told me it would be here tomorrow. What am I missing???
I would make them drain the pool to the light.
 

nizak

Senior Member
Is the #8 insulated considered an EGC? The back side of the forming shell has a bonding lug that was connected to rebar. The Insulated #8 which terminates in the pool j-box is reduced down to #12 from the branch circuit. Is the EGC in the rubber cord(#16) not a sufficient means to ground it? Thanks
 

bradleyelectric

Senior Member
Location
forest hill, md
Is the #8 insulated considered an EGC? The back side of the forming shell has a bonding lug that was connected to rebar. The Insulated #8 which terminates in the pool j-box is reduced down to #12 from the branch circuit. Is the EGC in the rubber cord(#16) not a sufficient means to ground it? Thanks

The light is installed as soon as the liner is in place in a liner pool or before the plaster in a gunite pool. The only time it is typical to install the light when the pool is filled is to change a broken fixture. Do not turn the light on till the pool is filled. They are made to be cooled by the water and wont last long if lit dry.

The insulated #8 is a bond. The insulated green in the SO is the EGC. Yes the #8 from the outside of the shell to the rebar is also a bond
 
Last edited:

WinZip

Senior Member
Have them drain the pool to below the light then pull the # 8 grd an light cord an install the 3m potting compound an let dry then fill the pool back up thats all you can do.
 

WinZip

Senior Member
if you buy a mirror that's attached to a small extension pole you can dip it in the water an see inside the nitch , I know because we had to do it twice before so the Inspector could see the compound so we didn't have to drain the pool.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Water-resistant cameras and camera housings aren't terribly expensive.


They're definitely than IR imaging cameras. :roll:
 