Ok any thoughts on this method? Take a trough, cut a larger opening, stub all your underground up into said trough, form around the trough and pour a concrete pad around the pipes tight to the bottom of the trough. Run tapcons from inside the trough into pad to "mechanically connect" everything together. For the most part it gets approved, but every once and awhile I'll run into a hiccup with an inspector. I'm just curious if I can get a few more arguments in my favor for this install. The most used code against this is....
Exception No. 2:? Raceways and cablesinstalled into the bottom of open bottom equipment, such as switchboards, motorcontrol centers, and floor or pad-mounted transformers, shall not be requiredto be mechanically secured to the equipment.
I've attached a drawing if my description is unclear. My two arguments back. Conduit connected to pad ---> pad connected to trough ---> mechanical connection. Also it may not be manufactured with an open bottom, but it is still equipment in terms of I now have it as part of my switch board. Who knows, maybe I'll find out that I shouldn't be doing it this way at all and will correct my ways.
*NOTE: I only apply this method with PVC underground as there is no need for electrical continuity to the raceway.
300.12Mechanical Continuity ? Raceways and Cables. Metal or nonmetallic raceways,cable armors, and cable sheaths shall be continuous between cabinets, boxes,fittings, or other enclosures or outlets.
Exception No. 1:? Short sections ofraceways used to provide support or protection of cable assemblies fromphysical damage shall not be required to be mechanically continuous.Exception No. 2:? Raceways and cablesinstalled into the bottom of open bottom equipment, such as switchboards, motorcontrol centers, and floor or pad-mounted transformers, shall not be requiredto be mechanically secured to the equipment.
*NOTE: I only apply this method with PVC underground as there is no need for electrical continuity to the raceway.