Someone asked me this today, open bottom switchboard with 7-4" EMT stubs into the bottom parallel 750's. 1600 amp feeder. What size single bonding jumper for all 7 raceways?
Sorry Aluminum 750's. Yes that is the question. The EGC's if used would be required to be up sized since 7 sets of 750 Al conductors are way oversized but I couldn't think of a code section that said explicitly that a raceway bonding jumper would also need to be up sized. There are no EGC's within the EMT.Interesting question, and one I am not sure that the code directly addresses.
I believe you are compliant with a single 4/0 copper bonding jumper, but could understand someone applying the parallel rule and require a full sized bonding conductor to each raceway.