BAYSEAL OC Light Density - Open Cell Foam with NM-B cable
The following document (link) shows that it is permissible, but with certain restrictions with regard to the wiring methods. I have a few questions that directly pertain to this as well as some other general questions while I'm at it...
https://www.nema.org/Technical/Documents/Bulletin%2095%20Rev%202007%20NM%20Cable%20encased%20in%20spray-foam%20insulation.pdf
First:
334.10(3) Other structures permitted to be of Types III, IV, and V
construction. Cables shall be concealed within walls,
floors, or ceilings that provide a thermal barrier of material
that has at least a 15-minute finish rating as identified
in listings of fire-rated assemblies.
When it refers to ceilings, it refers to the interior ceiling "covering", correct? Last I checked a ceiling is a ceiling, an attic is an attic, and a roof is a roof. Does it have to be an enclosed bay or can there be crawl space so long as the interior ceiling is 15 minute rated? I would think so, based on 334.23 (and therefore 320.23, followed by 300.4[D]). Someone is essentially trying to say that the NM-B needs to have a 360 deg 15 minute thermal barrier...
Next:
Section 334.80 requires ampacity adjustments for NM cables bundled and run through a bored hole that will be filled with insulation and for more than two NM cables that are installed in contact with thermal insulation without maintaining spacing between cables. Section 334.80 states that where more than two Type NM-B cables are run through a bored hole that is to be fire or draft stopped using thermal insulation or sealing foam, the ampacity must be adjusted. Section 334.80 also states that where more than two NM cables containing two or more current-carrying conductors are installed in contact with thermal insulation without maintaining spacing between cables, the allowable ampacity of each conductor shall be adjusted in accordance with Table 310.15(B)(2)(a).
I've read several threads on this forum in regard to this and there are so many varying explanations that I'd like a cut and dry confirmation of what I've learned. True or False?:
1) There is no specification for the distance of "spacing".
In my opinion they should change it to "not in contact" instead of "maintain spacing". A micron is a "space" under a microscope, but I doubt that would be enough "space".
2) "...where more than two NM cables containing two or more current-carrying conductors are installed in contact with thermal insulation without maintaining spacing between cables...".
I read this as: one 8/2 in contact with an 8/2 requires no derating. But an 8/2 in contact with an 8/3 requires derating.
Finally:
Regardless if it is politically correct, or wrong, or whatever, on many tract home jobs where one of the main concerns is "hurry up!", many apprentices are taught "rule of thumb" do's and don'ts without an explanation as to why. For instance, "It's okay to run up to three wires through a bored hole, but you can only put two wires under a staple." I searched the entire 2014 NEC for the word "bored" and couldn't find anything that would explain this "rule of thumb". I thought that maybe this was derived from 334.80. Any takers?
The following document (link) shows that it is permissible, but with certain restrictions with regard to the wiring methods. I have a few questions that directly pertain to this as well as some other general questions while I'm at it...
https://www.nema.org/Technical/Documents/Bulletin%2095%20Rev%202007%20NM%20Cable%20encased%20in%20spray-foam%20insulation.pdf
First:
334.10(3) Other structures permitted to be of Types III, IV, and V
construction. Cables shall be concealed within walls,
floors, or ceilings that provide a thermal barrier of material
that has at least a 15-minute finish rating as identified
in listings of fire-rated assemblies.
When it refers to ceilings, it refers to the interior ceiling "covering", correct? Last I checked a ceiling is a ceiling, an attic is an attic, and a roof is a roof. Does it have to be an enclosed bay or can there be crawl space so long as the interior ceiling is 15 minute rated? I would think so, based on 334.23 (and therefore 320.23, followed by 300.4[D]). Someone is essentially trying to say that the NM-B needs to have a 360 deg 15 minute thermal barrier...
Next:
Section 334.80 requires ampacity adjustments for NM cables bundled and run through a bored hole that will be filled with insulation and for more than two NM cables that are installed in contact with thermal insulation without maintaining spacing between cables. Section 334.80 states that where more than two Type NM-B cables are run through a bored hole that is to be fire or draft stopped using thermal insulation or sealing foam, the ampacity must be adjusted. Section 334.80 also states that where more than two NM cables containing two or more current-carrying conductors are installed in contact with thermal insulation without maintaining spacing between cables, the allowable ampacity of each conductor shall be adjusted in accordance with Table 310.15(B)(2)(a).
I've read several threads on this forum in regard to this and there are so many varying explanations that I'd like a cut and dry confirmation of what I've learned. True or False?:
1) There is no specification for the distance of "spacing".
In my opinion they should change it to "not in contact" instead of "maintain spacing". A micron is a "space" under a microscope, but I doubt that would be enough "space".
2) "...where more than two NM cables containing two or more current-carrying conductors are installed in contact with thermal insulation without maintaining spacing between cables...".
I read this as: one 8/2 in contact with an 8/2 requires no derating. But an 8/2 in contact with an 8/3 requires derating.
Finally:
Regardless if it is politically correct, or wrong, or whatever, on many tract home jobs where one of the main concerns is "hurry up!", many apprentices are taught "rule of thumb" do's and don'ts without an explanation as to why. For instance, "It's okay to run up to three wires through a bored hole, but you can only put two wires under a staple." I searched the entire 2014 NEC for the word "bored" and couldn't find anything that would explain this "rule of thumb". I thought that maybe this was derived from 334.80. Any takers?