Open/Close method for Motor Starter Box
I am trying to figure out the proper Opening and Closing method for a motor starter box. Currently I have a 4x fiberglass enclosure on order that is hinged with latches and an option for padlocking. I have someone here telling me it is required to have a "tool" to open and close the box but I can't seem to find any indication either way in the NEC code book.
The starter box has a contactor and overload rated for 480v going to a 60hp motor with FLA of 77Amps (disconnecting means are to be provided by the installer on the line side of the Motor Starter).
You won't find it in the NEC. It may be in the NFPA79. i think it only says a tool has to be used to open it. it can close without a tool (I think).
In any case, do the latches require a tool to open them? If you put a padlock on it, is the key not a tool? Even if you put a lead seal on it, the wire cutters you would use to break the seal is a tool.
Sounds like you are referring to something like a disconnect with mechanically-interlocked door, where you can't open the door (without "tool") unless the OPEN/CLOSE handle is in the OPEN position...???
I looked in NFPA79. Did no find it there.
Many industrial facilities have their own "internal standards" which require tools to be used to open equipment containing >240V.
These tools can be as simple as a Torx driver instead of a flat blade screw or a padlock.
It's in NFPA79. 6.2.3 for enclosures with disconnects, 6.2.4 for those without disconnects. Note: I have the 2007 edition.