Open Delta & Harmonics

Status
Not open for further replies.
Location
NE (9.06 miles @5.9 Degrees from Winged Horses)
Occupation
EC - retired
Local housing development has a common well that we are considering putting a VFD on. The pad mount transformer that feeds the 20 hp 230v three phase well also supplies power to at least two of the adjacent homes. Transformer is open wye open delta. I do not know the kva at this moment. Will/could there be a harmonics problem with this installation that may affect the homes?

Thanks
Tom
 

boater bill

Senior Member
Location
Cape Coral, Fl.
I would specify a 3% input line reactor from TCI or MTE to prevent harmonics to the line. The bus filter that comes with some of the VFD's is OK, but an external unit really helps.
 