Open Delta, High Leg

Status
Not open for further replies.
I have a service that is Open Delta, High Leg, served by 2-wire primary. I am comfortable with the fact that Phase A and C, with respect to ground, may be used for Lighting/Receptacle, and with the fact that 240V-3Phase can be utilized for loads. But, the question is, can 240V-Single Phase be used without restriction? Meaning, Phase B to C, and A to B? Any help will be most appreciated. All this assumes that the B-Phase is the high leg.
 
The only "prohibited" connection is from the high leg to the neutral.

Depending on the size of the individual transformers your utility may have some specific requirements for load balancing.
 
high leg

high leg

as far as the voltage goes it can be used without restriction..ie: CA, BA, BC...the only "glich" I can think of is you can not use a slash/rated breaker (240/120) when incorporating "B" phase. You must use a fully rated 240 volt breaker.
 
ctrane said:
But, the question is, can 240V-Single Phase be used without restriction? Meaning, Phase B to C, and A to B?
In theory, absolutely. In practice, note that there is more impedance, and thus less "stability" across the open side of the Delta. The high leg should have the lightest loading.

I have used an open Delta to supply two 3-pole breakers and three 2pole breakers in a 12-space panel, but I did make sure the smaller 2-pole loads used the high leg.

I could be wrong, but something I can't explain tells me that a larger proportion of 3-phase loading somehow helps stabilize the voltage across the open side of the Delta, but I have no evidence.
 
Thanks to all that have replied thus far, and look forward to all that will...One more question, how do you calculate loads for such a system? Do you just take the total kVA, and divide it by 240(root 3)? Should I calculate what is on each phase?
 