Open Delta Neutral

Status
Not open for further replies.

dcsva@aol.com

Senior Member
Location
Virginia
120/240VAC/3PH Open Delta
The 120volt loads are lights & receptacles
IMO, I feel that my thinking is correct to say that "Article 310-15,b,4,a" apply's.
The neutral conductor is not required to be counted.
Therefore, "TABLE 310-15,b,2,a" does not apply.
Does this sound right?
 
Re: Open Delta Neutral

First you say that it does apply. Then you say that it does not apply. No, that does not sound right. :confused:

I'm not sure how your system is wired. But in a 120 volt circuit, the neutral does count.
 