Hello everyone,
I have been requested to provide a fault calculation for a new 400 Amp single phase service. The service will feed from an Open Delta Bank consisting of a 100kVA lighter pot and a 50kVA power pot both with an impedance of 1.5%. The different calculators that I have available give a fault current of approx. 42,000 Amps at the secondary bushings. But since the service length will be around 75 feet of 1/0 overhead triplex with a #2 reduced neutral, I know that the fault current will be less at the meter base. I don't want to give the fault current at the transformer because it will force the contractor to install higher rated gear and cost more money. Any help would be appreciated on how to figure out the fault current at the meter base. Thank you.
I have been requested to provide a fault calculation for a new 400 Amp single phase service. The service will feed from an Open Delta Bank consisting of a 100kVA lighter pot and a 50kVA power pot both with an impedance of 1.5%. The different calculators that I have available give a fault current of approx. 42,000 Amps at the secondary bushings. But since the service length will be around 75 feet of 1/0 overhead triplex with a #2 reduced neutral, I know that the fault current will be less at the meter base. I don't want to give the fault current at the transformer because it will force the contractor to install higher rated gear and cost more money. Any help would be appreciated on how to figure out the fault current at the meter base. Thank you.