turbozoin
Member
- Location
- United States
I took a look at a friends house today just to give a thumbs up or down on his electrical system. Cutler Hammer panels, decent work, and most circuits are sound. However, one branch circuit feeding a couple duplex receptacles and lighting for two rooms, has an issue. My basic 3 light plug tester showed reverse polarity on the receptacles. I checked wiring in the boxes and the wires were landed accordingly, whites to proper side of recep and blacks to proper side of recep. I believe L and N were crossed up in a box upstream because I read voltage on the white wire with my NCVT and nothing on the black wire. I swapped them on the recep and then saw my 3 light plug tester read "Okay". Although, the middle light was bright and the second yellow light was dimly light. It was borderline and "open ground" reading. THEN, out came the fluke meter. Keep in mind, in this situation "L" is the white wire and "N" is the black wire in the box(terrible, I know...). 120v "L" to "N", 80v L to G, and 40v N to G. I have seen a similar issue before when a ground wasn't tied through upstream in a branch circuit. On that occasion, I saw an inadequate voltage from line to ground. But I don't remember seeing voltage on the neutral, it's possible I didn't test neutral to ground that previous occasion. Anyway, I will spend a little more time investigating the cause of this issue. I will find the problem. I just don't know when I'll have time to return to do so. Will the issue create a hazardous situation? Do I need to advise that my friend discontinues use of the said receptacles. Thanks to all who read my post, and good day.