The electron man
Senior Member
- Location
- Nyc
- Occupation
- Electrician
Hey so I recently installed 2 gfci outdoors and when I plug in the tester as seen in the pic's below I get an open ground Indication
I checked and I do have continuity between the ground and neutral so I know I have a ground fault path back to the main why am I getting and open ground then
View attachment 2574855
Yes I have 120v at the outlet inside where I jumped power from and outside at the gfciIs it actually a valid ground ? Did you check voltage to ground as well . If it was a valid ground you should have 120 volts to ground . Just because you get continuity between your grounded and grounding conductors at one location does not mean the path to ground is complete. You grounding and grounded conductors are at the same potential because they originate at the same place
Sent from my iPhone using Tapatalk
Can you explain thisIs it actually a valid ground ? Did you check voltage to ground as well . If it was a valid ground you should have 120 volts to ground . Just because you get continuity between your grounded and grounding conductors at one location does not mean the path to ground is complete. You grounding and grounded conductors are at the same potential because they originate at the same place
Sent from my iPhone using Tapatalk
Yes I have 120v at the outlet inside where I jumped power from and outside at the gfci
But the plug in tester as you see above indicates an open ground
Can you explain this
Just because you get continuity between your grounded and grounding conductors at one location does not mean the path to ground is complete
Once again, a solenoid tester, or even a bulb in a socket would be a better tester.
Do the test and reset buttons work? Did you try the plug-in tester elsewhere?
Check for power between the hot and the neutral; the tester or light should stay on.
Check for power between the hot and the ground; the tester or light should immediately trip the GFCI.
Do you have the black and white mis-wired anywhere?
I have 120v from neutral to hotOnce again, a solenoid tester, or even a bulb in a socket would be a better tester.
Do the test and reset buttons work? Did you try the plug-in tester elsewhere?
Check for power between the hot and the neutral; the tester or light should stay on.
Check for power between the hot and the ground; the tester or light should immediately trip the GFCI.
Do you have the black and white mis-wired anywhere?
What are you using to test your voltage?
Larry's post is important.
Multi meterWhat are you using to test your voltage?
Larry's post is important.
Sounds like the tester is bad.I plugged the tester in to 10 different outlets in different locations in my home and they all have the same indication open ground
Get a different plug-in tester. Yours may be bad, or one bulb isn't working.I plugged the tester in to 10 different outlets in different locations in my home and they all have the same indication open ground
Got it , if there's is no solid egc how do I get voltage from hot to ground ??Get a different plug-in tester. Yours may be bad, or one bulb isn't working.
That, or you truly don't have a solid ground (EGC) back to the panel.
I see what looks like BX in the pics and that never was a good grounding conductor.
Because standard voltmeters use so little current, which is why I suggest a solenoid tester (or bulb).Got it , if there's is no solid egc how do I get voltage from hot to ground ??
If you don't have a solenoid tester, then take a pigtail socket and put a bulb in it. One lead/tail to hot and the other to ground. If it doesn't light the bulb, the ground is not solid. I would suggest an incandescent bulb rather than an LED. The LED doesn't draw enough current.Got it , if there's is no solid egc how do I get voltage from hot to ground ??
Got it , if there's is no solid egc how do I get voltage from hot to ground ??
Because standard voltmeters use so little current, which is why I suggest a solenoid tester (or bulb).