Open Neutral

Status
Not open for further replies.

brian john

Senior Member
Location
Leesburg, VA
When install a UPS with input out put transformers and dual source inputs it is IMPERAITIVE the EC understand grounding rules and proper wiring. It appears the contractor left out a neutral connection and the EGC was carrying current. The structure has metal wall coverings the UPS rear cover screw was tight against the wall and it appears the structure was the path for the neutral current. This is the rear cover, note burn marks, I did not take a picture of the wall as we were on OT late at night with a limited work window for UPS replacement.

PIC11.jpg


PIC2.jpg


PIC3.jpg
 
At hospital installs I have noticed the neutral to be switched in the ats's making some of the 480 v readings to ground unconnected at the ats. Dangerous for electricians extremely.
 
I think the confusion arise here as these are auto transformers and have XO and HO common. I found the existing installation confusing to follow.
 