brian john
Senior Member
- Location
- Leesburg, VA
When install a UPS with input out put transformers and dual source inputs it is IMPERAITIVE the EC understand grounding rules and proper wiring. It appears the contractor left out a neutral connection and the EGC was carrying current. The structure has metal wall coverings the UPS rear cover screw was tight against the wall and it appears the structure was the path for the neutral current. This is the rear cover, note burn marks, I did not take a picture of the wall as we were on OT late at night with a limited work window for UPS replacement.