I had an open neutral situation last month that baffled me a bit.
The open neutral itself happened when the triplex going to the house snapped at an intermediate pole due to years of tree limb chafing (branch grew into the drop, stressed it, and finally the messenger snapped from fatigue.)
Anyway, the house was a typical rural situation. No metal water main and no gas line. The only connection to earth was 2 driven ground rods. The only possible other connection to earth was the EGC via the well pump, but I never checked to see if the EGC was bonded to the well casing or not.
So the symptoms were typical open neutral behavior. Lights dimming and brightening, fans running fast and slow, UPS on the computer kept kicking on and off, etc. I took voltage readings and they never fluctuated too wildly as I would have expected them to, and not enough to fry any electronic equipment. There was 4 amps of current on the GEC at one point when I took a measurement.
Also, keep in mind this went on for over a week with the messenger completely snapped. The only connection back to the poco transformer via the earth was via the ground rods and possibly the well casing. No equipment in the house was fried, though I'm guessing the UPS might have saved the computer.
So, it begs the question. I never thought that ground rods alone could stabilize the voltage enough to prevent catastrophic changes in voltage. Now I'm thinking they can.![Confused :confused: :confused:](data:image/gif;base64,R0lGODlhAQABAIAAAAAAAP///yH5BAEAAAAALAAAAAABAAEAAAIBRAA7)
The open neutral itself happened when the triplex going to the house snapped at an intermediate pole due to years of tree limb chafing (branch grew into the drop, stressed it, and finally the messenger snapped from fatigue.)
Anyway, the house was a typical rural situation. No metal water main and no gas line. The only connection to earth was 2 driven ground rods. The only possible other connection to earth was the EGC via the well pump, but I never checked to see if the EGC was bonded to the well casing or not.
So the symptoms were typical open neutral behavior. Lights dimming and brightening, fans running fast and slow, UPS on the computer kept kicking on and off, etc. I took voltage readings and they never fluctuated too wildly as I would have expected them to, and not enough to fry any electronic equipment. There was 4 amps of current on the GEC at one point when I took a measurement.
Also, keep in mind this went on for over a week with the messenger completely snapped. The only connection back to the poco transformer via the earth was via the ground rods and possibly the well casing. No equipment in the house was fried, though I'm guessing the UPS might have saved the computer.
So, it begs the question. I never thought that ground rods alone could stabilize the voltage enough to prevent catastrophic changes in voltage. Now I'm thinking they can.