I would like to hear how you guys do circuiting and load calculation for pre-wired furniture.
Maybe 220.14(H) (Fixed Multioutlet Assemblies) section could be used for pre-wired furniture, but I am not sure this is correct section to use.
Instead I take 500 Watts per workstation (one chair), 500 W cover 1 or 2 screens and PC. In this case, one 20A circuit is enough for three workstations.
Sometimes architectural plan shows 3 quads per workstation. You get 18 duplex for 3 workstations. If you take 180W per duplex, you get 3240W on one circuit. I don’t feel it is reasonable to take 180W per receptacle for pre-wired furniture system.
Do you think I am doing wrong calculation and violate any NEC section?
Maybe 220.14(H) (Fixed Multioutlet Assemblies) section could be used for pre-wired furniture, but I am not sure this is correct section to use.
Instead I take 500 Watts per workstation (one chair), 500 W cover 1 or 2 screens and PC. In this case, one 20A circuit is enough for three workstations.
Sometimes architectural plan shows 3 quads per workstation. You get 18 duplex for 3 workstations. If you take 180W per duplex, you get 3240W on one circuit. I don’t feel it is reasonable to take 180W per receptacle for pre-wired furniture system.
Do you think I am doing wrong calculation and violate any NEC section?