Have a switch gear 120v 208 2000 amp switchgear. Want to know if I need ppe when opening panel covers when circuit is live. Fed by 125 kva transformer.
When it's owned by the Utility?How does a 125kva transformer supply 2000 amp switchgear? Typically the highest incident energies will be on the line side of the first overcurrent protective device for the secondary of the transformer.
To close the loop on this for my own good... I do 70E compliance electrical safety classes and have done this for hundreds of participants over the past 5 years. I always offer that my email address is listed in the handout material, and if I can ever provide you with an incident energy level for PPE usage, just email me and I'm happy to do it. So given that premise, if I was asked what PPE to wear to access the secondary of a 125 kVA 208V transformer, I'd say 20 calories. I used a 13,200 Volt, 75 MVA strength source, and a 150 kVA transformer with standard impedance, and a 2-second timeout of any overcurrent protection, line or load side, I came up with 18.3 calories. I've seen 300 kVA transformers in PDUs in Data Centers with 40 calorie secondaries, 130 calorie secondaries of 2000 kVA transformers and everything in between. So based on that I think a 20 calorie PPE suit would suffice. Sure, wear a 40 if you have it, and if you don't need to do much with mobility, and if it's cool enough, but a 20 cal suit should suffice.When it's owned by the Utility?
The difficulty comes in determining the appropriate PPE. If it is in fact the service-entrance off the secondary of a 3-phase, 125 kVA transformer then one couldn't use the PPE Categories method 130.7(C)(15) in 70E because that assumes there's an upstream ocpd. It should work for the fault current limitations imposed by Table 130.7(C)(15)(a) since the fault current will be 125,000/208/1.732 = 347 amps divided by the transformer's nameplate impedance. If it's as low as 2% there's only 347/.02 = 17,350 amps using the infinite bus fault current calculation, which is less than the 25kA limiter in the table. But again this assumes there's an upstream ocpd.
I would request details about the service-entrance, like primary ocpd and Utility contribution numbers and model it in SKM for determination of incident energy and then suit up accordingly.
I question whether the situation is real because 125 kVA is not a typical size and could be referring to the old 125 kVA exemption from a couple code cycles back. That limitation has been reduced in IEEE 1584 to 2000 amps of bolted fault current, which is closer to around 25 kVA.
Thank you much appreciateTo close the loop on this for my own good... I do 70E compliance electrical safety classes and have done this for hundreds of participants over the past 5 years. I always offer that my email address is listed in the handout material, and if I can ever provide you with an incident energy level for PPE usage, just email me and I'm happy to do it. So given that premise, if I was asked what PPE to wear to access the secondary of a 125 kVA 208V transformer, I'd say 20 calories. I used a 13,200 Volt, 75 MVA strength source, and a 150 kVA transformer with standard impedance, and a 2-second timeout of any overcurrent protection, line or load side, I came up with 18.3 calories. I've seen 300 kVA transformers in PDUs in Data Centers with 40 calorie secondaries, 130 calorie secondaries of 2000 kVA transformers and everything in between. So based on that I think a 20 calorie PPE suit would suffice. Sure, wear a 40 if you have it, and if you don't need to do much with mobility, and if it's cool enough, but a 20 cal suit should suffice.
Not utility. This comes from customers side. 4160 coming in to step down to 120 208.When it's owned by the Utility?
The difficulty comes in determining the appropriate PPE. If it is in fact the service-entrance off the secondary of a 3-phase, 125 kVA transformer then one couldn't use the PPE Categories method 130.7(C)(15) in 70E because that assumes there's an upstream ocpd. It should work for the fault current limitations imposed by Table 130.7(C)(15)(a) since the fault current will be 125,000/208/1.732 = 347 amps divided by the transformer's nameplate impedance. If it's as low as 2% there's only 347/.02 = 17,350 amps using the infinite bus fault current calculation, which is less than the 25kA limiter in the table. But again this assumes there's an upstream ocpd.
I would request details about the service-entrance, like primary ocpd and Utility contribution numbers and model it in SKM for determination of incident energy and then suit up accordingly.
I question whether the situation is real because 125 kVA is not a typical size and could be referring to the old 125 kVA exemption from a couple code cycles back. That limitation has been reduced in IEEE 1584 to 2000 amps of bolted fault current, which is closer to around 25 kVA.
What is the real benefit of this? Our line side terminals are already required to be protected so I see no benefit to following the things they do in Canada. That photo looks pretty dumb not coming into the top of the panel.The Canadian model panels completely enclose service ent conductors , that our 408.3 (2) was going to follow suit a few cycles ago was exciting news. Only to find these international manufacturers cheesing it out in American markets , with corny little terminal covers.
View attachment 2557745
~RJ~
the trade's safety , us , you, me & every other spark reading here ...What is the real benefit of this?
How is really more safe? The terminals on the main are now required to be insulated so when the main CB is off there are no exposed live parts. For that reason I see no purpose for what is shown in the photo.the trade's safety , us , you, me & every other spark reading here ...
via the very same manufacturers that foist 'safety related' products and their subsequent updates upon the CMP's
70E could stay in the truck, along with the 12-20 cal suit & the osha man if we 'rated' the same as our northern counterparts
~RJ~
well, apparently the Canadians do InfinityFor that reason I see no purpose for what is shown in the photo.
How is really more safe? The terminals on the main are now required to be insulated so when the main CB is off there are no exposed live parts. For that reason I see no purpose for what is shown in the photo.
The way it is done in the states here you still technically have a live panel even with breaker off (OSHA standards). The Canadian method of isolating the service conductors makes it no longer a live panel with breaker off, no access to live conductors while working on branch circuits.well, apparently the Canadians do Infinity
~RJ~
bingo!The way it is done in the states here you still technically have a live panel even with breaker off (OSHA standards). The Canadian method of isolating the service conductors makes it no longer a live panel with breaker off, no access to live conductors while working on branch circuits.
Those two data points don't match. Sure, it is POSSIBLE to over size your switchgear by 300% or so, but really?Have a switch gear 120v 208 2000 amp switchgear. Want to know if I need ppe when opening panel covers when circuit is live. Fed by 125 kva transformer.
Correct me if i'm wrong Jraef, but aren't they (customer, GC, etc) supposed to 'sign off'...?You tell them that..
I read things like this often but where I work we do not follow NFPA70E nor do we have live work permits. And no one is using PPE to open a panel cover. If safety Sam walks by when you're working inside of a live panel all he cares about is your hard hat being on your head.You need PPE to open ANY switchgear that is live, the only issue is at what level.
You also need a Live Work Permit from whomever is in charge of safety for the organization you work for, because THEY need a Safe Electrical Work Practices program that would make SURE that you know all of this before you ever open or even think about opening a panel. The fact that you are asking means whomever you are doing this for is in violation of OSHA workplace requirements and if something bad happens, they can be held CRIMINALLY responsible. Ignorance is NOT an excuse either. You tell them that...
With all due respect Jraef, guru of all things motor/VFD related, The Energized Electrical Work Permit (EEWP) is not required if opening for inspection, but one must be suited to the correct PPE level.Those two data points don't match. Sure, it is POSSIBLE to over size your switchgear by 300% or so, but really?
You need PPE to open ANY switchgear that is live, the only issue is at what level.
You also need a Live Work Permit from whomever is in charge of safety for the organization you work for, because THEY need a Safe Electrical Work Practices program that would make SURE that you know all of this before you ever open or even think about opening a panel. The fact that you are asking means whomever you are doing this for is in violation of OSHA workplace requirements and if something bad happens, they can be held CRIMINALLY responsible. Ignorance is NOT an excuse either. You tell them that...