I am looking a drawing for a dust collector system and in the 1 line they spec a 225 kva 208 delta to 480 wye transformer feeding the VFD for the system
Does anyone know any reason why this could pose a problem in this situation? The tech that is ramrodding the job thinks this will cause problems with the VFD
due to inrush
I thought with a VFD set at a minute 20 seconds ramp time there would be little if any inrush?
He said it would cause the coil to collapse?
Can anyone give me some feed back on this topic
The transformer will be constantly energized and only the VFD will be operated on and off I guess I am confused and he couldn't explain why he had concerns
Does anyone know any reason why this could pose a problem in this situation? The tech that is ramrodding the job thinks this will cause problems with the VFD
due to inrush
I thought with a VFD set at a minute 20 seconds ramp time there would be little if any inrush?
He said it would cause the coil to collapse?
Can anyone give me some feed back on this topic
The transformer will be constantly energized and only the VFD will be operated on and off I guess I am confused and he couldn't explain why he had concerns