Hello to everyone. I am currently troubleshooting an operating room that keeps going into alarm on the (LIM) line isolation monitor.
This is a brand new room that was up and running for several weeks. Last week they had a bigger case than normal and brought in extra equipment. After the equipment was plugged in it went into alarm. The tech from the hospital went up and unplugged all unnecessary equipment. After that all the problems seemed to have started. The LIM would go from 2.7 milliamps down to .07. This continued throughout the surgery. I was called in to troubleshoot the problem. This is where I am at now with this room. If I plug in 3 particular pieces of equipment that is used daily in these rooms it will drive the LIM monitor into alarm as high as 7-8 milliamps then on its own fall back down to 2.4 milliamps or as low as .5 milliamps. Then on its own will drive right back up into alarm. This scenario will happen all day unless I unplug the equipment. All the equipment has been checked out and has been taken to other o.r. rooms with no problems. After checking all the wiring, plugs, connections ect. there are 3 things that have my attention and looking for some help on this.
1) I removed the ground bar from the isolation panel and had it floating with only the ground wires from the feed, the LIM and the transformer attached. With the bar floating it would go into alarm. If I removed just the ground wire coming from the feed the LIM would drop down to a normal reading and stay there. I put a megger on the feeder wires and all checked out. I even increased the ground wire size and temporary ran it to the ISO panel and still went into alarm.
2) I can only get the ISO panel LIM to fluctuate when I have these 3 pieces of equipment plugged in and turned on. I have tried the same type of equipment from other o.r. rooms and took this equipment to other rooms. The LIM still fluctuates.
3) When I had the ground bar floating, I reattached it over night with just the feeder, LIM and transformer ground wires attached. I left off all the branch circuit ground wires off. I did leave the 3 pieces of equipment plugged in and turned on.....I had over 75 alarms the next morning.
The list is very long of things I have tried. Too long to list. I can say that all the other o.r. rooms a functioning just fine and they are all feed out of the same panel. I did megger the ISO transformer also and that checked out ok. Any thoughts?? Any suggestions?? All is very much appreciated!
This is a brand new room that was up and running for several weeks. Last week they had a bigger case than normal and brought in extra equipment. After the equipment was plugged in it went into alarm. The tech from the hospital went up and unplugged all unnecessary equipment. After that all the problems seemed to have started. The LIM would go from 2.7 milliamps down to .07. This continued throughout the surgery. I was called in to troubleshoot the problem. This is where I am at now with this room. If I plug in 3 particular pieces of equipment that is used daily in these rooms it will drive the LIM monitor into alarm as high as 7-8 milliamps then on its own fall back down to 2.4 milliamps or as low as .5 milliamps. Then on its own will drive right back up into alarm. This scenario will happen all day unless I unplug the equipment. All the equipment has been checked out and has been taken to other o.r. rooms with no problems. After checking all the wiring, plugs, connections ect. there are 3 things that have my attention and looking for some help on this.
1) I removed the ground bar from the isolation panel and had it floating with only the ground wires from the feed, the LIM and the transformer attached. With the bar floating it would go into alarm. If I removed just the ground wire coming from the feed the LIM would drop down to a normal reading and stay there. I put a megger on the feeder wires and all checked out. I even increased the ground wire size and temporary ran it to the ISO panel and still went into alarm.
2) I can only get the ISO panel LIM to fluctuate when I have these 3 pieces of equipment plugged in and turned on. I have tried the same type of equipment from other o.r. rooms and took this equipment to other rooms. The LIM still fluctuates.
3) When I had the ground bar floating, I reattached it over night with just the feeder, LIM and transformer ground wires attached. I left off all the branch circuit ground wires off. I did leave the 3 pieces of equipment plugged in and turned on.....I had over 75 alarms the next morning.
The list is very long of things I have tried. Too long to list. I can say that all the other o.r. rooms a functioning just fine and they are all feed out of the same panel. I did megger the ISO transformer also and that checked out ok. Any thoughts?? Any suggestions?? All is very much appreciated!