david
Senior Member
- Location
- Pennsylvania
Comments please,
Back ground: Hospital operating room with out the presence of a lighting fixture on the normal branch for the hospital. All lighting in the room from the critical branch.
NFPA 90
6.3.2.2.11.1 One or more battery-powered lighting units shall be provided within locations
where deep sedation and general anesthesia is administered.
6.3.2.2.11.2 The lighting level of each unit shall be sufficient to terminate procedures intended
to be performed within the operating room.
6.3.2.2.11.3 The sensor for units shall be wired to the branch circuit(s) serving general lighting
within the room.
6.3.2.2.11.4 Units shall be capable of providing lighting for 1½ hours.
6.3.2.2.11.5 Units shall be tested monthly for 30 seconds, and annually for 30 minutes.
NFPA 99 Commentary:
Paragraph 6.3.2.2.11.1 requires supplemental battery-powered lighting in all areas where deep sedation
and general anesthesia are administered. Although these areas are also required to be served from
the EES, the momentary loss of lighting associated with the activation of the EES can be detrimental to
delivery of patient care in these spaces
NFPA 70/ 2008
517.19 Critical Care Areas. (A) Patient Bed Location Branch Circuits. Each patient bed location shall be supplied by at least two branch circuits, one or more from the emergency system and one or more circuits from the normal system. At least one branch circuit from the emergency system shall supply an outlet(s) only at that bed location. All branch circuits from the normal system shall be from a single panelboard.
517.63(A) Battery-Powered Emergency Lighting Units. One or more battery-powered emergency lighting units shall be provided in accordance with 700.12(F).
700.12(F).
(F) Unit Equipment.
The branch circuit feeding the unit equipment shall be the same branch circuit as that serving the normal lighting in the area and connected ahead of any local switches.
Back ground: Hospital operating room with out the presence of a lighting fixture on the normal branch for the hospital. All lighting in the room from the critical branch.
NFPA 90
6.3.2.2.11.1 One or more battery-powered lighting units shall be provided within locations
where deep sedation and general anesthesia is administered.
6.3.2.2.11.2 The lighting level of each unit shall be sufficient to terminate procedures intended
to be performed within the operating room.
6.3.2.2.11.3 The sensor for units shall be wired to the branch circuit(s) serving general lighting
within the room.
6.3.2.2.11.4 Units shall be capable of providing lighting for 1½ hours.
6.3.2.2.11.5 Units shall be tested monthly for 30 seconds, and annually for 30 minutes.
NFPA 99 Commentary:
Paragraph 6.3.2.2.11.1 requires supplemental battery-powered lighting in all areas where deep sedation
and general anesthesia are administered. Although these areas are also required to be served from
the EES, the momentary loss of lighting associated with the activation of the EES can be detrimental to
delivery of patient care in these spaces
NFPA 70/ 2008
517.19 Critical Care Areas. (A) Patient Bed Location Branch Circuits. Each patient bed location shall be supplied by at least two branch circuits, one or more from the emergency system and one or more circuits from the normal system. At least one branch circuit from the emergency system shall supply an outlet(s) only at that bed location. All branch circuits from the normal system shall be from a single panelboard.
517.63(A) Battery-Powered Emergency Lighting Units. One or more battery-powered emergency lighting units shall be provided in accordance with 700.12(F).
700.12(F).
(F) Unit Equipment.
The branch circuit feeding the unit equipment shall be the same branch circuit as that serving the normal lighting in the area and connected ahead of any local switches.