This is a data center with a somewhat generic looking L5-20 plug and connector body serving a IT rack. The operations staff indicates the plug and connector body are warm/hot, but has not told me the actual temperature yet, just that it is close to but below its continuous rating of 16A. The load profile is pretty flat, so I would guess it is hanging around at 15-16A 24/7.
If the terminations are good for 60deg C, what is an acceptable temp on the outside of the plug or connector body when I have an IR scan done?
The answer to that is "so hot that if you touch it you'll get burned".
Here's another datasheet:
http://www.legrand.us/~/media/produ...gs connectors 3 wire spec sheet sf1702r2.ashx
As you can see, Temperature Rise is 30C max @ 150% rated current.
30C=85F
If your room is 75F that's 75F+85F=160F. That's so hot that anyone touching it would be burned. Granted you're not loading it at 150% rated current but let's agree that any load will cause temperature rise. According to
NIST even at 111F a human feels like they're getting burned.
Some things you can consider:
Check your connections and wiring. Bad connections & wiring are the #1 cause of heat at a plug.
Go with a plug with a higher amperage rating.
Provide strain relief.
Hardwire the circuit.