Operation of 240 VAC Appliances on 208 VAC

Status
Not open for further replies.
Many apartment houses, condos, cluster homes, and modular home parks are served with two phases of a 208Y/120 volt system. Since a 240-volt heating appliance such as a kitchen range, clothes dryer, or water heater will operate at 75% of rated capacity when fed 208 VAC, should it be required that outlets for such appliances be clearly marked to inform the owner of the reduced voltage? Also, since a 12kW range will require a 60 ampere branch circuit if run on 208 volts, should the NEC be updated to consider this?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Many apartment houses, condos, cluster homes, and modular home parks are served with two phases of a 208Y/120 volt system. Since a 240-volt heating appliance such as a kitchen range, clothes dryer, or water heater will operate at 75% of rated capacity when fed 208 VAC, should it be required that outlets for such appliances be clearly marked to inform the owner of the reduced voltage? Also, since a 12kW range will require a 60 ampere branch circuit if run on 208 volts, should the NEC be updated to consider this?

Do you have a calculation for this?
 

iwire

Moderator
Staff member
Location
Massachusetts
Many apartment houses, condos, cluster homes, and modular home parks are served with two phases of a 208Y/120 volt system. Since a 240-volt heating appliance such as a kitchen range, clothes dryer, or water heater will operate at 75% of rated capacity when fed 208 VAC, should it be required that outlets for such appliances be clearly marked to inform the owner of the reduced voltage? Also, since a 12kW range will require a 60 ampere branch circuit if run on 208 volts, should the NEC be updated to consider this?

All residential electric ranges, dryers and water heaters that I can recall had two ratings, one at 208 and the other at 240.
 

kbsparky

Senior Member
Location
Delmarva, USA
...Since a 240-volt heating appliance such as a kitchen range, clothes dryer, or water heater will operate at 75% of rated capacity when fed 208 VAC... Also, since a 12kW range will require a 60 ampere branch circuit if run on 208 volts, should the NEC be updated to consider this?

You answered your own question in your original stipulation --- such appliances will operate at 75% of their rating. Therefore, a 12 kW range will now be a 9 kW range, and at that level will only require 43? Amps at max capacity.

Even at that, I believe that a single range is allowed to be supplied by a 40 Amp circuit.
 