Fred B
Senior Member
- Location
- Upstate, NY
- Occupation
- Electrician
Would you consider this?
NEMA 14-50 with 75o C terminals.
8/3 MC, MFG lists wire as THHN/THWN-2. 90oC
15ft run to 50A breaker 75oC terminal.
Application for electric range.
#8 3conductor cable listed as 50A in 75o Column in table 310.16
NEMA 14-50 with 75o C terminals.
8/3 MC, MFG lists wire as THHN/THWN-2. 90oC
15ft run to 50A breaker 75oC terminal.
Application for electric range.
#8 3conductor cable listed as 50A in 75o Column in table 310.16