jameselectric said:
Yes there is conduit. I think this was done back in the 1950's. It looks as if the 100 amp panel can is ALREADY attached to the neutral in the service.
OK. This makes more sense.
The 100 Amp fuse center should have been connected (if it wasn't, originally) to the water service, by the Codes of the Fifties and Sixties. I agree that re-establishing the Grounding Electrode System is required.
jameselectric said:
So If i would just put in 2 ground rods (#6) and bond the water pipe(#4) it would be better.
When the client has limited funds, don't sell him oversized copper. Revisit 2005 NEC Table 250.66. I suspect you only need #8.
jameselectric said:
Some one had tapped the line side and installed some regular breakers (30 amp for water heater and another for a dryer).
Back in the mid 1900s split bus residential service centers were very popular. Be sure, first, that the breaker subpanel tap, in fact, is bogus. It may just be another set of Service Disconnects -- there can be six, total. If the subpanel feeder conductors are added to a lug that already has another conductor in it, then that's a problem to correct, for sure.
jameselectric said:
it would be nice to get rid of those fuses but like i said the money would be an issue.
In my opinion, the real issue is the capacity of the service. That's been increased. 24 kW is a nice amount for a simple upgrade from an older, smaller original K&T service. However, this already happened half a century ago, sounds like. Electric hot water and electric clothes dry indicate additional loading above and beyond anything that original system could have handled. Be sure to calculate the existing load to be sure that this 100 Amp service is loaded within capacity.
The fact that the overcurrent protection is fuses is only an end user convenience item. I'm not trying to start a fuse vs. CB debate, only to state that conversion from fuse to CB is a poor first use of limited funds.
Identify any "heavy" loads on the existing K&T branch circuits (such as window AC, Refrigerator, laundry machine, electric heater, the kitchen counter that the coffee maker & toaster are at, etc.) and spend the money on new circuits to these spots.
Shed the "heavy" load off the K&T branch circuits. Don't sweat the small stuff.
jameselectric said:
Would it be code compliant to just run a ground wire to the attic lets say a #10 or # 8 copper (the largest branch breaker is a 30 amp and it goes back to the panel 3 wire dryer the rest are 15 amp) to a centrally located j-box and just drop #12 to the few gfci receptacles instead of running each ground wire all the way back to panel?? This would make this a whole lot easier and faster if its legal but I keep coming up with "all circuit conductors have to be in the same conduit/cable etc.."
Revisit section 300.3(B)(2) and follow the references, first to 250.134(B)Exception No.1 and then to 250.130(C).
jameselectric said:
just drop #12 to the few gfci receptacles
Again, with limited funds, don't use a larger gauge than the branch circuit is already wired with.
jameselectric said:
run a ground wire to the attic lets say a #10
It only needs to be equal to the largest Equipment Grounding Conductor.