First post here, I work on the industrial maintenance side as a plant electrician for a water treatment plant. Some of you may know me and this post from electriciantalk. 310.12 is tripping me up a little. I get that if a service/feeder is supplying the entire residential load then the wire can be downsized. Part (c) is tripping me up. The way I read it no feeder in a single dwelling needs to be bigger than 83 percent of the service rating. For example if you have a 200 amp service fed with 2/0 copper there is no need to use larger than 2/0 in any other feeders. That doesn't seem to be the consensus with more knowledgeable poeple. Can I gather some opinions on this.
 

jaggedben

Senior Member
Location
Northern California
Occupation
Solar and Energy Storage Installer
Yes, you have it correct. What else would it mean? And what reason could there be for a downstream feeder to be bigger than an upstream one (other than additional power sources on site) ?
 

Greentagger

Senior Member
Location
Texas
Occupation
Master Electrician, Electrical Inspector
Poorly written. Language focuses so much on entire load of the dwelling.
 

texie

Senior Member
Location
Fort Collins, Colorado
Occupation
Electrician, Contractor, Inspector
First post here, I work on the industrial maintenance side as a plant electrician for a water treatment plant. Some of you may know me and this post from electriciantalk. 310.12 is tripping me up a little. I get that if a service/feeder is supplying the entire residential load then the wire can be downsized. Part (c) is tripping me up. The way I read it no feeder in a single dwelling needs to be bigger than 83 percent of the service rating. For example if you have a 200 amp service fed with 2/0 copper there is no need to use larger than 2/0 in any other feeders. That doesn't seem to be the consensus with more knowledgeable poeple. Can I gather some opinions on this.
You have it correct. This often occurs when you have a meter/main that has breaker spaces as well as feed through lugs to feed an inside panel.
 

mburtis

Member
Location
Wyoming
Occupation
Water plant electrician
Well I'm glad for that. I'm trying to help a buddy fix his sketchy garage panel so we can run a feed to his barn. Has a meter and 200 amp main breaker which originally feed the interior 200 amp panel via 2/0 copper. At some point they added a little exterior panel to run the garage and the ac but they just ran #4 copper over to the main breaker and stuffed it in on top of the 2/0. My plan is to replace the small exterior panel with a 200 amp feed thru, feed it with 2/0 from the main, then hook the 2/0 feeder to the interior panel up to the feed thru lugs.
 