Good morning,
I've been pouring through the NEC regs for non-conductive communications cable (Fiber) and High voltage raceways, but haven't found anything stating this can/can't done.
I have a comm path prone to freezing, and this year it has taken out one of my SMF feeds to the university. I'm pricing out an alternative path, but do currently have one available I could utilize.
The issue is it's part of my 13.2kV feeder between buildings. I technically have separate raceways (only 1 of 6 6" conduits are in use) but I need to traverse two high voltage vaults between the buildings, and exit the HV enclosures.
770.133 and 620.36 I believe state I can run fiber along side conductors <600v, but this is a different case.
Would 15kV rated innerduct from point A-B traversing the vaults and all HV spaces be considered a separate race, and as such allow this by code?
Thank you for your knowledge,
Travis
I've been pouring through the NEC regs for non-conductive communications cable (Fiber) and High voltage raceways, but haven't found anything stating this can/can't done.
I have a comm path prone to freezing, and this year it has taken out one of my SMF feeds to the university. I'm pricing out an alternative path, but do currently have one available I could utilize.
The issue is it's part of my 13.2kV feeder between buildings. I technically have separate raceways (only 1 of 6 6" conduits are in use) but I need to traverse two high voltage vaults between the buildings, and exit the HV enclosures.
770.133 and 620.36 I believe state I can run fiber along side conductors <600v, but this is a different case.
Would 15kV rated innerduct from point A-B traversing the vaults and all HV spaces be considered a separate race, and as such allow this by code?
Thank you for your knowledge,
Travis