I have 3 strings of 15 modules one unit.
Each string of modules has 15 optimizer so it’s one optimizer per string.
I have total of three units from inverter. That’s total 18 DC conductors in one conduit.
The maximum output current of the optimizer is 15A according to datasheet. Optimizer is Power Optimizer P400.
Question:
1. I am using #8 THWN -2 up to junction box. So based on roof temp correction factor local temp is 34 Celsius and rooftop is add 22 Celsius so it’s 56 Celsius which is 71%. Conduit fill is total 18 so it’s 50%. #8 THWN-2 is 50A so 50x.71x.50 = 17.75A. So now in order to check #8 is ok should I take maximum output current optimizer 15A or should do max output currentx1.25 which is 15x1.25=18.825?
Each string of modules has 15 optimizer so it’s one optimizer per string.
I have total of three units from inverter. That’s total 18 DC conductors in one conduit.
The maximum output current of the optimizer is 15A according to datasheet. Optimizer is Power Optimizer P400.
Question:
1. I am using #8 THWN -2 up to junction box. So based on roof temp correction factor local temp is 34 Celsius and rooftop is add 22 Celsius so it’s 56 Celsius which is 71%. Conduit fill is total 18 so it’s 50%. #8 THWN-2 is 50A so 50x.71x.50 = 17.75A. So now in order to check #8 is ok should I take maximum output current optimizer 15A or should do max output currentx1.25 which is 15x1.25=18.825?