Article 702.5 states "An optional stanby system shall have adequate capacity and rating for the supply of all equipment intended to be operated at one time." the article goes on to say that "the user of the optional standby system shall be permitted to select the load connected to the system."
I am installing a 25kw (104 output amps) generator in a residence with a 200 amp sevice. I believe I can install a 200 amp automatic transfer switch and connect the 25kw generator to the existing loadcenter. I believe that the the generator does not have to be sized according to the load calculation of the residence (171 amps) because the code allows for the user to select the loads connected to the system. Most homes in Florida have an air handler with a electric heat strip and an air conditioning compressor controllled by a thermostat common to both units. However the heat strip and the air conditioning compressor do not operate at the same time and they are non-coincidental loads. If the user elects not to select the heat strips (2 @ 10kw, the range (12kw) and the electric water heater (4.8kw) then the standby generator has adequate capacity and rating to supply all equipment intended to be used at one time. Have I interpreted this code article correctly, I am having difficulty convincing the local building department.
I am installing a 25kw (104 output amps) generator in a residence with a 200 amp sevice. I believe I can install a 200 amp automatic transfer switch and connect the 25kw generator to the existing loadcenter. I believe that the the generator does not have to be sized according to the load calculation of the residence (171 amps) because the code allows for the user to select the loads connected to the system. Most homes in Florida have an air handler with a electric heat strip and an air conditioning compressor controllled by a thermostat common to both units. However the heat strip and the air conditioning compressor do not operate at the same time and they are non-coincidental loads. If the user elects not to select the heat strips (2 @ 10kw, the range (12kw) and the electric water heater (4.8kw) then the standby generator has adequate capacity and rating to supply all equipment intended to be used at one time. Have I interpreted this code article correctly, I am having difficulty convincing the local building department.