Existing single family home, one 120/240 V service (400A/320 continuous) supplies 3 subpanels: pool, upstairs, and downstairs.
Seems like the optional method can be used for service calculations, but not for the feeder calcs, based on 220.82(A):
"...total connected load served by a single 120/240-volt or 208Y/120-volt set of 3-wire service or feeder conductors..."
Reason for asking this question about an existing system is that at least one of the subpanel feeders was grossly undersized for the load that is connected to it, and I'm making sure that I'm accurately calculating what it should have been, when I give report to the owners. (I'll probably make a separate post with those details).
Thanks in advance
Seems like the optional method can be used for service calculations, but not for the feeder calcs, based on 220.82(A):
"...total connected load served by a single 120/240-volt or 208Y/120-volt set of 3-wire service or feeder conductors..."
Reason for asking this question about an existing system is that at least one of the subpanel feeders was grossly undersized for the load that is connected to it, and I'm making sure that I'm accurately calculating what it should have been, when I give report to the owners. (I'll probably make a separate post with those details).
Thanks in advance