Really need to be clear as to which type of standby power or generator purpose, The definition or scope really changes everything:
Article 700 Emergency System in 700.12 has the requirement of "within 10 Seconds" for Emergency power
700.1 Scope
This article applies to the electrical safety of the installation, operation, and maintenance of emergency systems consisting of circuits and equipment intended to supply, distribute, and control electricity for illumination, power, or both, to required facilities when the normal electrical supply or system is interrupted.
701 Legally required Standby system in 701.12 has a requirement of "not to exceed 60 seconds"
701.1 Scope
The provisions of this article apply to the electrical safety of the installation, operation, and maintenance of legally required standby systems consisting of circuits and equipment intended to supply, distribute, and control electricity to required facilities for illumination or power, or both, when the normal electrical supply or system is interrupted.
702 Optional standby systems have no such time requirement.
702.1 Scope
The provisions of this article apply to the installation and operation of optional standby systems.
The systems covered by this article consist of those that are permanently installed in their entirety, including prime movers, and those that are arranged for a connection to a premises wiring system from a portable alternate power supply..
Many times a HO wants an "emergency generator" but in reality it is an optional standby generator even though they want it because of medical devices or refrigeration.
If your inspector is asking for a "10 seconds" requirement does your generator purpose meet the requirements of article 700? And not an optional standby system article 702?