Hello everyone,
I've never used the optional calculation for multi-famliy dwellings, so I am not 100% sure this is correct. Here's the situation:
34 apartments @ 846 sq. ft. with the following equip:
2 small appliance circuit
1 laundry circuit
12 KW range
5 KW dryer
1500 W A/C
1200 W A/C
4000 W water heater
NO HEATING LOADS
So far I have 366,723VA without house loads.
House Load = 11520 VA
TOTAL = 378,243 VA according to Part II of art. 220
My interpretation of 220.32 is the following
994,092 VA's in the appartments, plus 11,520 VA house loads for a grand total of 1,005,612 @ 30% = 301,683.60 VA. Does this sound right?