I have seen this posted on other forums, but I don't believe anyone has cited where exactly it came from. I've installed many 20KW Generacs and have never seen this in any of the documentation that came with the generator/ATS nor in the PDFs available online.
Where did you quote that from and are you sure it applies to the generators sold today?
Thank you.
It is located in all RTS transfer switch installation books that come with the transfer switch, not the installation book for the generator.
MD posted a typical installation book (Even with the newer Nexus control system) that is supplied with all Generac RTS type transfer switchs, the wiring diagram (page 9-11) in this PDF is typical of of all Generac RTS ATS wire ups, the only exception is the change of battery charger system and where it is located, when they used to supply the wall wart type (no plug just the lamp cords coming out of it)
At one time the instruction had us installing them in the generator cabinet at the battery, and supplying it with a circuit from the house panel, later they supplied the terminals and a fuse block to connect them in the transfer switch with a tap to one of the load terminals and neutral, they even included the jumper wires crimp on female spade terminals, screws and male spade terminal to do this, and the charger output hooked to 194/15B + and 0 - this back fed the battery through these terminals, the 0 terminal is also tied to the cabinet of the generator for a negative grounding of the battery, when they came out with the Nexus controller they built a float charger system right on the main mother board in the generator, so no external charger is needed.
There is a 178 and 183 terminals on some Generac generators, in most cases you will not use them, they are for remote switch automatic starting for use with a manual transfer switch
Interesting, on all of the Guardians I have installed over the years (none lately though) the charger has always been out at the generator, either piggy backed with the sense wires, or a separate set of 240 volt wires for the charger, and then the set of 12 Vdc wires to control the transfer switch as you mentioned. The 12 Vdc controls a simple cube relay, nothing electronic, so I don't think there would be sufficient induced voltage to affect the controls on longer runs, so it's kinda odd Generac would limit it to 30'. But then they do some strange stuff to begin with!:lol:
The electronics is all in the generator, the main controller board is located in the metal box behind where you land your wires, it will have a cover over it, N1 and N2 are an input to this controller and 23 is a -12vdc output to the transfer switch TR relay (ice cube relay) 194/15 is just the positive from the battery that also runs through the 7.5 amp fuse on the generator switch panel, the battery supplies all the power for the controller and the power up to the TR relay, the TR relay switches the set of solenoids that pull the transfer switch one way or the other, these are DC coils fed through a full wave bridge rectifier from the line voltage (240vac), the power to transfer to generator is derived from E-1 and E-2 which is the hots from the generator, this is to keep the transfer switch from transferring to the generator if it is not running or the breaker on it is tripped or off, the transfer to utility coil is fed through the same bridge rectifier but the limit switches will now have it connected to the N1A and N2A which is the utility side of the transfer switch, again if there is no utility power it will not transfer back.
I would presume that the input to the main controller board could be of a high enough impedance that N1 and N2 could pick up some capacitive coupling and if this happens while generator is running it could trigger the system to think that power is restored and transfer back, this could cause it to start cycling back and forth??? that is about the only thing I could see happening, but if it did it could be bad?