For outdoor panels we've got:
A contractor on one of our jobs just installed these four new subpanels and is seeking options. The guys did it, the boss later the water line, shutoff valve and hose bib.
It's a retrofit situation, and the panels are where they are because of existing conductor lengths, the need to newly separate new panels from the gas per utility rules, and other considerations that make any other location pretty unworkable. The two pipes to the right are the new underground feed (the old feeds were tangled up with the gas cluster to the left).
Local gas rules don't allow the feeders be extended above the gas meters, and the interior route for the extended feeders runs into a closet if the panels are located any further right.
Options?
The best I've come up with is to move the two panels right by two inches, the claim working space is 30" wide but not centered on the panels.
The center 2 inches with the water pipe is thus not within the working space.
CEC 2025 based on NFPA70 NEC 2023
110.26(E)(2)(c) Dedicated Equipment Space.
The space equal to the width and depth of the equipment, and extending from grade to a height of 1.8 m (6 ft) above the equipment, shall be dedicated to the electrical installation. No piping or other equipment foreign to the electrical installation shall be located in this zone.
A contractor on one of our jobs just installed these four new subpanels and is seeking options. The guys did it, the boss later the water line, shutoff valve and hose bib.
It's a retrofit situation, and the panels are where they are because of existing conductor lengths, the need to newly separate new panels from the gas per utility rules, and other considerations that make any other location pretty unworkable. The two pipes to the right are the new underground feed (the old feeds were tangled up with the gas cluster to the left).
Local gas rules don't allow the feeders be extended above the gas meters, and the interior route for the extended feeders runs into a closet if the panels are located any further right.
Options?

The best I've come up with is to move the two panels right by two inches, the claim working space is 30" wide but not centered on the panels.
The center 2 inches with the water pipe is thus not within the working space.