So I think we all know that MLO service panelboards are now prohibited under the 2020 NEC. Couple of questions:
1. The wording for meter centers is a little different where "separate compartments" are allowed where for panelboards, its "separate enclosures". Has anyone heard of any discussions between the manufacturers, product standard people (UL?), and NFPA/NEC about options for redesigned MLO service panelboards that would allow separate compartments? While I dont support the nixing of MLO's, I think it as absurd how there has never been any requirement for covering or protecting the bus and lugs in panelboards. I could see something along the lines of what what I-line does as being mandatory.
2. Consider you typical application of where you would have used something like a 1000A MLO service panelboard with 6 200's to feed your branch panels. Has anyone priced out/thought about doing that with 6 separate circuit breaker enclosures (or fused safety switches) instead of just getting a main breaker panelboard? The main breaker pretty much doubles the cost. Last one I did similar to this it was about $4500 for the MLO and $9k with a main breaker, so there is the potential for significant cost savings.
1. The wording for meter centers is a little different where "separate compartments" are allowed where for panelboards, its "separate enclosures". Has anyone heard of any discussions between the manufacturers, product standard people (UL?), and NFPA/NEC about options for redesigned MLO service panelboards that would allow separate compartments? While I dont support the nixing of MLO's, I think it as absurd how there has never been any requirement for covering or protecting the bus and lugs in panelboards. I could see something along the lines of what what I-line does as being mandatory.
2. Consider you typical application of where you would have used something like a 1000A MLO service panelboard with 6 200's to feed your branch panels. Has anyone priced out/thought about doing that with 6 separate circuit breaker enclosures (or fused safety switches) instead of just getting a main breaker panelboard? The main breaker pretty much doubles the cost. Last one I did similar to this it was about $4500 for the MLO and $9k with a main breaker, so there is the potential for significant cost savings.