How to get 90 minutes.
How to get 90 minutes.
The emergency generator will take over with in 10 seconds and then would have to run for the 90 minutes. Aren't the ballasts to ensure that there is no loss of lighting during the switch over.
NFPA 101 31-1.3.8 Periodic Testing of Emergency Lighting Equipment states: A functional test shall be conducted on every required emergency lighting system at 30-day intervals for a minimum of 30 seconds. An annual test shall be conducted for the 1 ?-hour duration. Equipment shall be fully operational for the duration of the test. Written records of testing shall be kept by the owner for inspection by the authority having jurisdiction.